This project is a reboot of this [[MainsFrequency|earlier main frequency counter]], aiming for more accuracy and lower latency. | This project is a reboot of this [[MainsFrequency|earlier main frequency counter]], aiming for more accuracy and lower latency. | ||
This has been achieved by using an ESP32c3 board with the 'phasing' algorithm described below. | |||
No mains interfacing hardware is required, measurement data can be easily transferred using MQTT over a WiFi network. | |||
=== Concept === | === Concept === | ||
| Line 27: | Line 27: | ||
* https://www.electroschematics.com/voltage-sensor/ | * https://www.electroschematics.com/voltage-sensor/ | ||
=== Phasing algorithm === | |||
* Sample the mains frequency waveform during | The algorithm is as follows: | ||
* | * Sample the mains frequency waveform continuously at 5000 Hz | ||
* | * Correlate each sample with a perfect 50 Hz reference waveform, by keeping a sum of the waveform multiplied by a cosine (I) and a sum of the waveform multiplied by a sine (Q) | ||
* | * For each second, calculate the phase using the accumulated I and Q sums with atan2(Q, I). | ||
* The change in phase during one second is directly proportional to the frequency deviation from the 50 Hz reference frequency | |||
This results in: | |||
* A continuous process, with a new frequency value every second | |||
* The algorithm uses *all* of the data contained in one second (there is no single threshold value), thus producing a robust value | |||
* Any DC offset in the mains frequency waveform is automatically balanced out, no need to keep track of the median or quartile values | |||
=== Zero cross algoritm === | |||
This is my older idea for an algorithm to get accurate instantaneous frequency: | |||
* During approximately 100 ms, sample the mains frequency waveform and store it in a buffer. | |||
* Calculate the median, lower and upper quartiles of the waveform amplitude data | |||
* During approximately 1000 ms, sample the waveform and apply a linear regression algorithm on the waveform value (shifted by the median value) | |||
* The linear regression algorithm is active in between the lower and higher quartile values and calculates an interpolated zero crossing of the waveform (with sub-sample resolution) | |||
* Keep track of the first and the 50th interpolated zero-crossing time, then calculate the frequency from the time difference | |||
-> this should give about 1 millihertz frequency resolution in one second | -> this should give about 1 millihertz frequency resolution in one second | ||
== Visualisation == | == Visualisation == | ||
| Line 48: | Line 52: | ||
* publish frequency as a number over WiFi / MQTT for visualization as a graph-over-time on our grafana server | * publish frequency as a number over WiFi / MQTT for visualization as a graph-over-time on our grafana server | ||
* idea: directly on a LED ring. The ring shows an integer number (e.g.) of 50 Hz cycles, with the color of the pixel indicating the analog value | * idea: directly on a LED ring. The ring shows an integer number (e.g.) of 50 Hz cycles, with the color of the pixel indicating the analog value | ||
* just show the relative phase angle on the LED ring, this could be a single bright pixel for the latest phase measurement and progressively dimmer pixels for older phase measurements. | |||
=== Mains waveform ring === | === Mains waveform ring === | ||
| Line 65: | Line 70: | ||
[[File:luatos_esp32c3_pinout.png|right|thumb|ESP32c3 luatos board pinout]] | |||
=== Luatos ESP32C3 === | |||
This module (I recommend the one with serial chip) seems to work quite well so far: | |||
* Senses mains waveform from surroundings with just a wire into its ADC input, using the 'phase' software algorithm | |||
* Clock crystal appears to be accurate, ESP32c3 datasheet claims it requires a 10 ppm crystal (or 0.5 mHz at 50Hz). Measured value corresponds to https://mainsfrequency.com | |||
* Has WiFi, works with WifiManager library, so can easily push measurements to MQTT over WiFi for example | |||
* Inexpensive, only 3 euros or so | |||
The ADC1/UART1 RX pin is the input for 50 Hz. You can just leave that unconnected and it will pick up 50 Hz, or perhaps connect a short piece (20 cm or so) of wire to it. | |||
=== Using ZMPT101B (old idea) === | |||
For measurement with an ESP8266, like a Wemos D1 mini or nodemcu, you need to put a 180k ohm resistor in line with the output from the ZMPT101B to the A0 input. | For measurement with an ESP8266, like a Wemos D1 mini or nodemcu, you need to put a 180k ohm resistor in line with the output from the ZMPT101B to the A0 input. | ||
The A0 input already has a 220k/100k resistive divider, effectively becoming a 400k/100k resistive divider with the series resistor, scaling down the 0-5V range to the 0-1V range required for the ADC on the ESP8266. | The A0 input already has a 220k/100k resistive divider, effectively becoming a 400k/100k resistive divider with the series resistor, scaling down the 0-5V range to the 0-1V range required for the ADC on the ESP8266. | ||
| Line 95: | Line 112: | ||
https://github.com/bertrik/MainsFrequency | https://github.com/bertrik/MainsFrequency | ||
To flash the | To flash the esp32c3 board: | ||
* install platformio | * install platformio | ||
* enter the | * check out the code | ||
cd | git clone https://github.com/bertrik/MainsFrequency | ||
* compile and upload | * enter the esp32c3phase directory | ||
cd MainsFrequency | |||
cd esp32c3phase | |||
* connect the board, compile and upload | |||
pio run -t upload | pio run -t upload | ||
* connect with serial terminal, to watch frequency measurements | |||
pio device monitor | |||
== Integration into revspace sensor infrastructure == | |||
There is a measurement device present at revspace (above the green tool board). It sends frequency data to the revspace MQTT server once every 5 seconds. | |||
Processing of this data into something that our grafana can display is unfortunately broken (is that documented somewhere anyway!?), see: | |||
https://revspace.nl/grafiekjes/d/3deykmVmz/power?orgId=1&refresh=1m | |||
You can watch the data (using mosquitto for example): | |||
mosquitto_sub -h revspace.nl -t revspace/sensors/ac/frequency -v | |||
Example data: | |||
topic = "revspace/sensors/ac/frequency", payload = "50.025 Hz" (retained) | |||
In the #revspace IRC channel, you can issue a command to show the most recently known value: | |||
!netfrequentie | |||
(where is the script that handles this?) | |||
Example data: | |||
23:00 <@bertrik> !netfrequentie | |||
23:00 <@bar> bertrik: 49.898 Hz | |||
Revision as of 09:29, 19 September 2023
| Last Update | 2023-09-19 |
This has been achieved by using an ESP32c3 board with the 'phasing' algorithm described below. No mains interfacing hardware is required, measurement data can be easily transferred using MQTT over a WiFi network.
Concept
Desired end result:
Phasing algorithm
- Sample the mains frequency waveform continuously at 5000 Hz
- Correlate each sample with a perfect 50 Hz reference waveform, by keeping a sum of the waveform multiplied by a cosine (I) and a sum of the waveform multiplied by a sine (Q)
- For each second, calculate the phase using the accumulated I and Q sums with atan2(Q, I).
- The change in phase during one second is directly proportional to the frequency deviation from the 50 Hz reference frequency
This results in:
- A continuous process, with a new frequency value every second
- The algorithm uses *all* of the data contained in one second (there is no single threshold value), thus producing a robust value
- Any DC offset in the mains frequency waveform is automatically balanced out, no need to keep track of the median or quartile values
Zero cross algoritm
Visualisation
- just show the relative phase angle on the LED ring, this could be a single bright pixel for the latest phase measurement and progressively dimmer pixels for older phase measurements.
Mains waveform ring
Concepts:
Calculation:
Luatos ESP32C3
- Senses mains waveform from surroundings with just a wire into its ADC input, using the 'phase' software algorithm
| GND | GND | Ground |
| VCC | 5V | Powers the ZMPT101B from the wemos D1 mini |
| OUT | A0 | Analog mains waveform, 0..5V, 180 kohm resistor in series |
- install platformio
- check out the code
- enter the esp32c3phase directory
cd MainsFrequency cd esp32c3phase
- connect the board, compile and upload
- connect with serial terminal, to watch frequency measurements
pio device monitor
Processing of this data into something that our grafana can display is unfortunately broken (is that documented somewhere anyway!?), see: https://revspace.nl/grafiekjes/d/3deykmVmz/power?orgId=1&refresh=1m
Example data:
!netfrequentie
(where is the script that handles this?) Example data:
23:00 <@bertrik> !netfrequentie 23:00 <@bar> bertrik: 49.898 Hz