GridFrequency
Project MainsFrequency2.0
Last Update 2023-05-31
Concept
Desired end result:
  • get more accurate frequency measurement, aiming for 1 milli-Hertz accuracy
  • get more responsive frequency measurement, i.e. instantaneous value (1 second), not a running average over 50 seconds.
Algoritm
Algorithm for getting accurate instantaneous frequency:
  • Sample the mains frequency waveform during approximately 100 ms
  • Determine the median, lower and upper quartiles of the waveform amplitude data
  • During approximately 1000 ms, sample the waveform, applying an amplitude shift according to the median, to make the waveform symmetric around zero
  • While sampling, run a state machine to perform a linear regression around the zero-crossing of the wavefrom. The start and end point of this regression are the lower and higher quartile.
  • Use the linear regression to calculate the interpolated time of the zero-crossing (the regression gives sub-sample resolution). Keep track of the first and last zero-crossing time.
  • Calculate the frequency from the time difference between the interpolated zero-crossings
Ideas
  • While playing around with an STM32 blue pill, it turned out you might not need a mains power interface at all. A piece of wire picks up ambient 50 Hz already. Typical accuracy of the STM32 clock crystal appears a bit lower than that of the ESP8266, but for visualisation this might not be so important. We don't need the WiFi-functionality of the ESP8266 if just visualizing. This simplifies things: required hardware is just bluepill + piece-of-wire + RGB LED ring.
  • A raspberry pi pico appears to be able to satisfy many requirements:
    • Able to sample mains frequency directly from ambient signals on its sensitive A/D input, without the need for a transformer circuit
    • Able to sample a signal with good timing accuracy, it has a crystal better than 30 ppm (0.0015 Hz at 50 Hz)
    • Might allow control of a LED ring using FastLED for visualisation (not possible with STM32), to be researched
    • Has WiFi support, although rather dodgy on the Arduino platform, for publishing directly to mqtt
    • Relatively inexpensive
Visualisation
  • publish frequency as a number over WiFi / MQTT for visualization as a graph-over-time on our grafana server
  • idea: directly on a LED ring. The ring shows an integer number (e.g.) of 50 Hz cycles, with the color of the pixel indicating the analog value
Mains waveform ring
Concepts:
  • The LED ring shows the raw waveform over time. Position along the ring is time, intensity/color is based on the instantaneous value of the mains voltage. So (for example) three 50 Hz cycles show up as 3 dark spots and 3 light spots around the ring, approximately 120 degrees apart. Basically it shows the phase compared to a reference 50 Hz frequency.
  • The LED ring is drawn based on a reference time (derived from the crystal oscillator), assumed to be exactly 50 Hz. A slightly fast mains waveform results in a clockwise rotation of the waveform pattern, a slightly slow mains waveform results in a counter-clockwise rotation of the waveform pattern.
  • Use a colourful gradient, not just intensity. Example: https://github.com/FastLED/FastLED/wiki/Gradient-color-palettes
Calculation:
  • Mains frequency is nominally 50 Hz, so period is 20 ms (0.02 sec)
  • With three waveforms around the ring, the ring represents 60 ms of mains signal
  • Intended LED ring has 24 RGB LEDs, so 60ms / 24 LEDs = 2.5 ms per LED. So we could sample the waveform at 400 Hz, and put 1 sample on each LED.
  • Example: 16 LED ring -> sample frequency 266.66.. Hz, or sample at 800 Hz and average 3 samples/LED
  • Example: 40 LED ring -> sample frequency 666.66.. Hz, or sample at 2000 Hz and average 3 samples/LED
  • Example: 45 LED ring -> sample frequency 750 Hz
  • Example: 60 LED ring -> sample frequency 1000 Hz
Connections
ZMPT101B Wemos D1 mini Remark
GND GND Ground
VCC 5V Powers the ZMPT101B from the wemos D1 mini
OUT A0 Analog mains waveform, 0..5V, 180 kohm resistor in series
To flash the esp8266:
  • install platformio
  • enter the esp8266sampler directory
 cd esp8266sampler
  • compile and upload