GridFrequency
Project MainsFrequency2.0
Last Update 2023-07-19
Concept
Desired end result:
  • get more accurate frequency measurement, aiming for 1 milli-Hertz accuracy
  • get more responsive frequency measurement, i.e. instantaneous value (1 second), not a running average over 50 seconds.
Zero cross algoritm
Algorithm for getting accurate instantaneous frequency:
  • During approximately 100 ms, sample the mains frequency waveform and store it in a buffer.
  • Calculate the median, lower and upper quartiles of the waveform amplitude data
  • During approximately 1000 ms, sample the waveform and apply a linear regression algorithm on the waveform value (shifted by the median value)
  • The linear regression algorithm is active in between the lower and higher quartile values and calculates an interpolated zero crossing of the waveform (with sub-sample resolution)
  • Keep track of the first and the 50th interpolated zero-crossing time, then calculate the frequency from the time difference
Phasing algorithm
Alternative algorithm:
  • Sample the mains frequency waveform at about 5000 Hz
  • Correlate during 1 second with a perfect 50 Hz reference waveform, by keeping a sum of the waveform multiplied by a cosine (I) and a sum of the waveform multiplied by a sine (Q)
  • After one second, calculate the phase using, atan2(Q, I). Changes in the phase compared to the previous second represent the deviation / time shift from the perfect 50 Hz frequency.
This results in:
  • continuous process, with a new frequency value every second
  • we use *all* of the data contained in one second, a condition for producing a robust value
  • any DC offset in the mains frequency waveform is automatically balanced out, no need to keep track of the median or quartile values
Ideas
  • While playing around with an STM32 blue pill, it turned out you might not need a mains power interface at all. A piece of wire picks up ambient 50 Hz already.
    • Typical accuracy of the STM32 clock crystal appears a bit lower than that of the ESP8266, but for visualisation this might not be so important.
    • You cannot do this with the Wemos D1 mini board (containing an ESP8266), because the A/D input has voltage-level matching resistors attached that pull it towards ground
  • A raspberry pi pico appears to satisfy many requirements:
    • Able to sample mains frequency directly from ambient signals on its sensitive A/D input, without the need for a transformer circuit
    • Able to sample a signal with good timing accuracy, it has a crystal better than 30 ppm (0.0015 Hz at 50 Hz)
    • Might allow control of a LED ring using FastLED for visualisation (not possible with STM32), to be researched
    • Has WiFi support, although rather dodgy on the Arduino platform, for publishing directly to mqtt
    • Relatively inexpensive
  • We can probably run the stats-collecting and frequency-calculating processes in parallel, continuously.
    • The frequency-calculating process can copy a snapshot of the quartile values when needed, to get a recent set, but keep decision-levels stable while running.
Visualisation
  • publish frequency as a number over WiFi / MQTT for visualization as a graph-over-time on our grafana server
  • idea: directly on a LED ring. The ring shows an integer number (e.g.) of 50 Hz cycles, with the color of the pixel indicating the analog value
Mains waveform ring
Concepts:
  • The LED ring shows the raw waveform over time. Position along the ring is time, intensity/color is based on the instantaneous value of the mains voltage. So (for example) three 50 Hz cycles show up as 3 dark spots and 3 light spots around the ring, approximately 120 degrees apart. Basically it shows the phase compared to a reference 50 Hz frequency.
  • The LED ring is drawn based on a reference time (derived from the crystal oscillator), assumed to be exactly 50 Hz. A slightly fast mains waveform results in a clockwise rotation of the waveform pattern, a slightly slow mains waveform results in a counter-clockwise rotation of the waveform pattern.
  • Use a colourful gradient, not just intensity. Example: https://github.com/FastLED/FastLED/wiki/Gradient-color-palettes
Calculation:
  • Mains frequency is nominally 50 Hz, so period is 20 ms (0.02 sec)
  • With three waveforms around the ring, the ring represents 60 ms of mains signal
  • Intended LED ring has 24 RGB LEDs, so 60ms / 24 LEDs = 2.5 ms per LED. So we could sample the waveform at 400 Hz, and put 1 sample on each LED.
  • Example: 16 LED ring -> sample frequency 266.66.. Hz, or sample at 800 Hz and average 3 samples/LED
  • Example: 40 LED ring -> sample frequency 666.66.. Hz, or sample at 2000 Hz and average 3 samples/LED
  • Example: 45 LED ring -> sample frequency 750 Hz
  • Example: 60 LED ring -> sample frequency 1000 Hz
Connections
ZMPT101B Wemos D1 mini Remark
GND GND Ground
VCC 5V Powers the ZMPT101B from the wemos D1 mini
OUT A0 Analog mains waveform, 0..5V, 180 kohm resistor in series
Luatos ESP32C3
ESP32c3 luatos board pinout
This module (with serial chip) seems to work quite well so far:
  • Senses mains waveform under some circumstances even without a wire attached, using the 'phase' software algorithm
  • Clock crystal appears to be accurate, ESP32c3 datasheet claims it requires a 10 ppm crystal (or 0.5 mHz at 50Hz). Measured value corresponds to https://mainsfrequency.com
  • Has WiFi, works with WifiManager library, so can easily push measurements to MQTT over WiFi for example
  • Inexpensive, only 3 euros or so
The ADC1/UART1 RX pin is the input for 50 Hz. You can just leave that unconnected and it will pick up 50 Hz, or perhaps connect a short piece (20 cm or so) of wire to it.
To flash the esp32c3 board:
  • install platformio
  • check out the code
 git clone https://github.com/bertrik/MainsFrequency
  • enter the esp32c3phase directory
 cd MainsFrequency
 cd esp32c3phase
  • connect the board, compile and upload
  • connect with serial terminal, to watch frequency measurements
 pio device monitor